消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

稳压泵设计流量

根据《消防给水及消火栓系统技术规范》GB50974-2014中5.3.3(1):“稳压泵的公称流量不应小于消防给水系统管网的正常泄漏量和系统自动启动流量”,但2024的教材上写的“不应小于正常泄漏量且应小于系统自动启动流量”。哪个是正解,或者他们说的是高位水箱的流量开关吗?

哇咔 | 2024-06-17 22:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

陈曲 2024-06-18 09:49 00 [回复]举报

按规范

应该大于他们相加

最帅游客 2024-06-18 10:07 00 [回复]举报

两种表述都是对的。小于泄漏量稳压泵会频繁启动。另外,前期的消防用水是用的高位消防水箱的水,如果稳压泵流量小于系统自启动流量,用于启泵的压力开关/流量天关就无法启泵。

个人理解,互相探讨,一起学习。

哇咔   回复: 最帅游客2024-06-18 10:39

那如果稳压泵的流量大于启动流量,那流量开关不就动作了吗?连锁水泵也就启了呀。本来没有火灾,就是稳压,怎么大泵还启了呢?

0    0 [回复]举报

最帅游客   回复: 哇咔2024-06-21 10:02

稳压泵流量大于启泵流量只是要求,平时系统内水基本不流动,不会让流量开关动作。只是发生火情的时候,喷头破裂或者消火栓出水的情况下,流量会大于流量天关设定值,从而启泵。



0    0 [回复]举报

香.香 2024-06-18 10:13 10 [回复]举报

稳压泵的公称流量不应小于消防给水系统管网的正常泄漏量但应小于系统的自动启动流量。这是正确的。在《消防给水及消火栓系统技术规范》上说的是很久以前没有统一的时候的说法,后面在通用规上对稳压泵的公称流量又有新的定义。从稳压泵的工作原理上就不难理解出,稳压泵的公称流量应小于系统的自动启动流量。

哇咔   回复: 香.香2024-06-18 10:40

这样我也能理解新教材,我也觉得新教材说的更明白一点儿。

0    0 [回复]举报

黄-江西省景德镇市 2024-06-18 13:38 10 [回复]举报

假设官网泄流量为1L/s,流量开关启泵流量为3L/s,那么1L/s<稳压泵流量<3L/s。

关闭

关闭

手机APP下载