七氟丙烷全淹没式灭火系统,灭火剂释放后会在室内下沉吗?

实际工程中七氟丙烷以一定的速度释放,均匀充满全室,还会因为灭火剂气体比空气重的重力作用下沉,积聚在地面或者说地面上的浓度较高吗?还是在浸渍时间内会出现高浓度向低浓度扩散直至全室灭火剂浓度均匀的现象?事故排风系统仅仅只需要将排风口设置在房间下部排除残余的灭火剂吗?

zzyzy | 2024-06-02 20:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

黄-江西省景德镇市 2024-06-03 12:07 10 [回复]举报

空气的分子质量约为29,七氟丙烷的分子质量约为170,气态下空气密度小于七氟丙烷。七氟丙烷(一下简称气体)释放后,气体会由于密度大于空气而沉底,逐渐叠升达到浸渍效果。浸渍时间内气体会逐渐达到均衡浓度。事故后排风系统的排风口不仅需要设置在沿墙面下部,还需要设置机械送风(补风)或墙面上部设置自然补风口,目的是使防区内形成空气对流让有害气体更有效的置换出去。类似排烟风机和补风机的原理。

zzyzy   回复: 黄-江西省景德镇市2024-06-03 15:56

感谢您的回答!也就是说在释放时灭火剂会先沉底,然后逐渐叠升充满全室,释放结束后然后高浓度区域向低浓度区逐渐扩散,然后整个室内的浓度均匀,也就不会有很明显的重气分层现象,对吗

0    0 [回复]举报

黄-江西省景德镇市   回复: zzyzy2024-06-04 12:38

可以这么理解,实际上气体喷出后,不可能完全把室内空气挤出,气体与空气的混合气体会在上部空间,其密度低于下部,因此下部气体浓度会比上部高一点。

0    0 [回复]举报

黄辉 2024-06-04 08:38 00 [回复]举报

七氟丙烷喷放后在防护区内气化成气态,由于七氟丙烷灭火剂喷放时有一定的动能,且发生火灾的防护区存在热烟气卷积等,灭火剂会快速的充满整个防护区。

七氟丙烷的分子重量比空气中,最终会慢慢的沉积到防护区下部,导致防护区下部七氟丙烷的浓度高,上部的浓度低。

因此,事故排风系统将排风口设置在房间下部,可以最大量的排除残余的灭火剂。


zzyzy   回复: 黄辉2024-06-04 17:50

好的,谢谢您的回答,我在做灭火剂的模拟,发现他全室均匀了,并没有想象中的因为重力作用使得建筑下部的浓度高于建筑上部,以为是灭火剂具有一定的动能与空气掺混的非常均匀了呢,导致现在的现象,那看来是我的模拟还是有些错误

0    0 [回复]举报

黄辉   回复: zzyzy2024-06-05 08:18

七氟丙烷灭火系统有浸渍时间要求。

3.3.8 灭火浸渍时间应符合下列规定:
1 木材、纸张、织物等固体表面火灾,宜采用20min;
2 通讯机房、电子计算机房内的电气设备火灾,应采用5min;
3 其他固体表面火灾,宜采用10 min;
4 气体和液体火灾,不应小于1 min。


长时间后,七氟丙烷分子质量大,由于重力,还是会导致防护区下部的浓度高于上部。

0    0 [回复]举报