消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

厂房自然排烟问题:当单层厂房高度为20米时,自然排烟窗最防烟分区最远距离按30米走,还是按2.8倍走?主要现在厂房宽度70米了。两侧有窗按三十米走,中间无法排烟了。

麻烦问一下各位,当单层厂房高度为20米时,自然排烟窗最防烟分区最远距离按30米走,还是按2.8倍走?主要现在厂房宽度70米了。两侧有窗按三十米走,中间无法排烟了。

天天蓝TTL | 2024-09-02 19:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

LHH2737 2024-09-03 10:25 10 [回复]举报

先说结论:不满足规范要求。

规范原文:防烟分区内任一点与最近的自然排烟窗(口)之间的水平距离不应大于30m。当工业建筑采用自然排烟方式时,其水平距离不应大于建筑内空间净高的2.8倍;

意思就是30m和净高的2.8倍都要满足,哪个数字小就以哪个为设计标准。

倜圳 2024-09-03 11:40 00 [回复]举报

顶上开排烟天窗啊

武汉建筑胖子 2024-09-09 10:56 00 [回复]举报

    根据《建筑防烟排烟系统技术标准》GB 51251-2017   4.3.2条  防烟分区内自然排烟窗(口)的面积、数量、位置应按本标准第4.6.3条规定经计算确定,且防烟分区内任一点与最近的自然排烟窗(口)之间的水平距离不应大于30m。当工业建筑采用自然排烟方式时,其水平距离尚不应大于建筑内空间净高的2.8倍;当公共建筑空间净高大于或等于6m,且具有自然对流条件时,其水平距离不应大于37.5m。所以30米和2.8倍都需要满足。

    我最近的一个项目也是你这种情况,是施工图基本完成后,在其他专业改动最小的考虑下,选择的是无动力风帽,但是根据18J621-3第53页,直径800的无动力风帽有效排烟面积仅有0.6平方米,就会导致在考虑结构已经画好的屋面檩条情况下进行布置非常多的风帽。所以这种情况有条件的话在前期提资的时候建筑暖通一定需要沟通好,最好加气楼或者排烟窗,这样排烟效果更好。

潘天坤 2024-09-10 08:33 10 [回复]举报

空间净高不大于10.7米的场所,按照30米执行;空间净高大于10.7米的场所按照净高的2.8倍执行(10.7*2.8=29.96米)

烟规编制组有个复函,有提到空间净高大于10米的场所,可以按照2.8倍执行,然后考虑到10.7*2.8比较接近30米,不少人认为可以放大到10.7米

建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准
上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

关闭

关闭

手机APP下载