泡沫罐胶囊的使用年限一般为6-7年?

泡沫罐胶囊的使用年限一般为6-7年,这是那个标准规范的条文要求?

消防网友77714 | 2024-04-27 10:26
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

灭邪斩 2024-05-02 09:28 10 [回复]举报

对于泡沫罐胶囊的使用年限,国标没有统一规定。

       泡沫灭火系统技术标准 GB50151-2021,11.0.11每半年应对下列项目进行检查,检查内容及要求应符合下列规定:4 应对压力式比例混合装置的胶囊进行检查,发现破损应及时更换。对于压力式比例混合器胶囊是其关键部件,若胶囊发生损坏,泡沫液泄漏,意味着整个系统瘫痪。因此,要对胶囊进行检查,确保其完好无损。

      国标要求半年一查,损坏应及时更换。同时还要遵守地方相关规定。