消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

气体灭火系统中排烟风机启动逻辑

大型交换机房的气体灭火系统中,排烟风机是如何启动的?

宁静致富 | 2024-03-06 09:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

黄辉 2024-03-07 10:08 00 [回复]举报

同一保护对象,不可兼得的气体灭火系统和排烟系统!


建议参考这个文章。


灭火后的通风换气,参考以下条文,在认为判定火灾已扑灭的情况下,手动启动。


气体灭火系统设计规范 GB50370-2005 


6.0.4 灭火后的防护区应通风换气,地下防护区和无窗或设固定窗扇的地上防护区,应设置机械排风装置,排风口宜设在防护区的下部并应直通室外。通信机房、电子计算机房等场所的通风换气次数应不少于每小时5次。

喜欢晴天 2024-03-07 15:29 00 [回复]举报

气体灭火区域的风机主要作用是平时换气和事故后排烟,所以在消防领域只有停止逻辑,没有启动逻辑。

在气体灭火剂喷洒前,风机应停止,避免灭火剂的浓度被降低,影响灭火效果。

南明离火 2024-03-09 09:05 00 [回复]举报

气体灭火防护区 只有 事故排风

潘天坤 2024-07-01 00:27 00 [回复]举报

当设置在灭火剂释放前必须关闭通风系统、防护区开口的气体灭火系统时,可以将排烟系统改为气体灭火后的机械排风(事故通风),但是注意气体灭火后的机械排风应设置在防护区的下部

当设置排烟系统 (包括自然排烟系统和机械排烟系统)时,不应采用火灾自动报警系统联动启动的方式自动开启系统排烟,以保证灭火系统实施有效灭火

建筑防火通用规范条文说明提及:对于建筑中上述需要设置排烟系统的场所,当设置气体灭火系统等在灭火剂释放前必须关闭通风系统、防护区开口的灭火系统时,允许将排烟系统改为事故通风系统,当设置排烟系统 (包括自然排烟系统和机械排烟系统)时,不应采用火灾自动报警系统联动启动的方式自动开启系统排烟,以保证灭火系统实施有效灭火

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

关闭

关闭

手机APP下载