雨淋阀组和预作用阀组

雨淋阀组和预作用阀组可以组合在一起吗,怎么工作求指导

任楚 | 2024-02-28 09:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

喜欢晴天 2024-03-07 16:59 00 [回复]举报

雨淋阀一般用于使用开式喷头的场所,可以理解为雨淋阀动作以后,水就直接喷洒出来,好处在于喷头出水速度快,比如水喷雾、细水雾、水幕。

动作逻辑一般设计为着火区域的火灾探测器触发火警后,联动阀组的电磁阀启动,电磁阀启动整个阀组,水由供水侧进入系统侧,喷头立刻喷水灭火。

预作用阀使用的是闭式喷头,系统侧的管网平时是充满压力气体的。一般用于场所的火灾类型适用水灭火系统,但是一旦被水淹会造成重大损失,系统侧的管网平时是充满压力气体的。比如古董家具、电脑机房等。也可以用来代替干式系统,比如严寒、高温场所。

动作逻辑一般设计为着火区域的火灾探测器触发火警后,联动阀组的电磁阀启动,电磁阀启动整个阀组,水由供水侧进入系统侧,管网排气,原来充满空气的管网转变为充满水的管网,此时如果真的发生火灾,喷头的玻璃柱破裂,喷头喷水灭火。如果是火灾探测器误报,喷头不动作。

你可以理解为预作用阀是雨淋阀和湿式报警阀的组合,所以雨淋阀和预作用阀再组合起来没有任何意义。