电气防火的问题

请教老师,低压开关不允许安装在可燃物上,是出自哪个标准规范?谢谢

消防网友30777 | 2023-09-11 16:39
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

安洪全 2023-09-11 16:56 10 [回复]举报

您说的是这条吗?

“建筑设计防火规范 GB50016-2014(2018年版) 10.2.4 开关、插座和照明灯具靠近可燃物时,应采取隔热、散热等防火措施。     

卤钨灯和额定功率不小于100W的白炽灯泡的吸顶灯、槽灯、嵌入式灯,其引入线应采用瓷管、矿棉等不燃材料作隔热保护。     

额定功率不小于60W的白炽灯、卤钨灯、高压钠灯、金属卤化物灯、荧光高压汞灯(包括电感镇流器)等,不应直接安装在可燃物体上或采取其他防火措施。



消防网友30777   回复: 安洪全2023-09-12 09:42

谢谢,空气开关可以直接按在木板上吗?

0    0 [回复]举报

安洪全   回复: 消防网友307772023-09-13 13:08

木板=可燃物,所以参照规范要求,不可以

1    0 [回复]举报

消防网友30777   回复: 安洪全2023-09-14 08:52

谢谢

0    0 [回复]举报

yizhongdayang 2023-09-12 09:08 30 [回复]举报

《建筑内部装修设计防火规范》 GB50222-2017/4.0.17 建筑内部的配电箱、控制面板、接线盒、开关、插座等不应直接安装在低于B1级的装修材料上;用于顶棚和墙面装修的木质类板材,当内部含有电器、电线等物体时,应采用不低于B1级的材料。

消防网友30777   回复: yizhongdayang2023-09-14 08:56

谢谢,很对应的条款,谢谢您

0    0 [回复]举报

张治福 2023-09-13 10:14 10 [回复]举报

一、建筑内部装修设计防火规范 GB50222-2017

4.0.17 建筑内部的配电箱、控制面板、接线盒、开关、插座等不应直接安装在低于B1级的装修材料上;用于顶棚和墙面装修的木质类板材,当内部含有电器、电线等物体时,应采用不低于B1级的材料。


消防网友30777   回复: 张治福2023-09-14 08:57

谢谢,很对应的条款,谢谢您

0    0 [回复]举报