商场下沉式广场最少需要设置一部疏散楼梯。请问设置自动扶梯当做疏散楼梯是否可行?依据哪条规范?

请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

安洪全 2023-07-27 13:49 30 [回复]举报

建规中未把自动扶梯纳入疏散宽度,地铁和人防将自动扶梯纳入了计算宽度。

所以您套用之前先要确定建筑的属性,如果不是人防或地铁建筑,就不应将自动扶梯的宽度计算在内。


建筑设计防火规范 GB50016-2014(2018年版)

5.5.4 自动扶梯和电梯不应计作安全疏散设施。


人民防空工程设计防火规范 GB50098-2009

3.1.7 设置本规范第3.1.6条3款1项的下沉式广场时,应符合下列规定:    

1 不同防火分区通向下沉式广场安全出口最近边缘之间的水平距离不应小于13m,广场内疏散区域的净面积不应小于169㎡。    

2 广场应设置不少于一个直通地坪的疏散楼梯,疏散楼梯的总宽度不应小于相邻最大防火分区通向下沉式广场计算疏散总宽度。    

3 当确需设置防风雨棚时,棚不得封闭,并应符合下列规定:     

1)四周敞开的面积应大于下沉式广场投影面积的25%,经计算大于40㎡时,可取40㎡;     

2)敞开的高度不得小于1m;      

3)当敞开部分采用防风雨百叶时,百叶的有效通风排烟面积可按百叶洞口面积的60%计算。    

4 本条第1款最小净面积的范围内不得用于除疏散外的其他用途;其他面积的使用,不得影响人员的疏散。     注:疏散楼梯总宽度可包括疏散楼梯宽度和90%的自动扶梯宽度。


建筑防火通用规范 GB55037-2022

7.5.1 地铁车站中站台公共区至站厅公共区或其他安全区域的疏散楼梯、自动扶梯和疏散通道的通过能力,应保证在远期或客流控制期中超高峰小时最大客流量时,一列进站列车所载乘客及站台上的候车乘客能在4min内全部撤离站台,并应能在6min内全部疏散至站厅公共区或其他安全区域。

张牙舞爪的张   回复: 安洪全2023-07-28 20:39

谢谢!