内衬风管新规消防设施通用规范 GB55036-2022是不是取消了土建风井内的内衬风管?

新规消防设施通用规范 GB55036-2022是不是取消了土建风井内的内衬风管?到底现在的风井是否需要安装内衬风管,这规范说的模棱两可,说是取消了《建筑防烟排烟系统技术标准》GB 51251-2017第3.3.7、4.4.7、不得采用土建风道。那到底现在土建风道能用吗,还是还的内衬风管?

消防网友65069 | 2023-04-20 13:59
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

冀消专 2023-04-20 17:38 00 [回复]举报

目前不强制,后续规范什么要求不可而知。

潘天坤 2024-07-09 08:35 00 [回复]举报

土建风道一般无法达到“内表面光滑、不漏风”,无法保证管道的密闭性能

消防防设施通用规范 GB55036-2022正文要求“内表面光滑、不漏风、”,实施指南要求“摩阻系数、气密闭性应符合系统送风和排烟要求”

土建风道的气密闭性能不太好测试,测试也不准确,如果被提出要求证明的话,一般也无法证明

同时烟规GB51251关于土建风道的相关要求,很多人认为目前旧技术标准中被废止的条文如果与通用规范不存在冲突,在新技术标准修订之前还可以暂时作为非强制性条文执行