消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

提问关于两用一备消火栓自动启泵逻辑

向各位老师请教一个问题,2022年一消补考题(题目不能100%肯定,大体是这个意思)。

室内消火栓设计流量为45L每秒,泵组采用2用一备,单台消火栓设计泵扬程和压力满足要求,设计流量为45L每秒。问是如何自动启泵的?

考前,听过一位网课老师讲是,低压压力开关动作后启动第一台泵,启泵后压力上升;火势增大后,使用消火栓数量持续增加,流量增大,压力再次降低,低压压力开关再次发信号,然后启动第二台泵。不知道这个说法正确不,请各位老师们能够不吝赐教,万分感谢!

在路上_pQrS | 2023-04-13 20:49
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

南明离火 2023-04-15 17:23 00 [回复]举报

图纸正常是同时启动两台泵

消防老胡 2023-04-15 19:57 10 [回复]举报

答案不唯一,低压压力开关动作后,可以启动第一台消防泵或者第1-2台消防泵。随着消防用水量的加大(也有可能消防泵自身及供电、交流接触器、二次控制回路等故障因素),主管压力再次降低,低压压力开关继续给消防泵配电控制柜控制回路常开点(带自锁)闭合,启动第二台或第三台消防泵。

在路上_pQrS 2023-04-19 12:33 00 [回复]举报

感谢两位老师的回答

冀消专 2023-04-20 17:44 00 [回复]举报

不对,既然两用就同时启动两台。

关闭

关闭

手机APP下载