消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

新人请教关于稳压泵和流量开关的问题。

按照书上所写,稳压泵的设计流量要大于流量开关的自启动压力,那么假设稳压泵的启动流量是4L每秒,流量开关的动作流量是3L每秒,那稳压泵启动补压,稳压泵的启动瞬间压力,难道不会触发流量开关启动消防水泵吗,因为在设计上稳压泵的流量要比流量开关大。

五月_fqYl | 2023-04-11 08:39
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

陈曲 2023-04-13 09:01 00 [回复]举报

有没有一种可能 稳压泵是靠压力启动的 这样想是不是豁然开朗了 

唐唐 2023-04-18 15:04 00 [回复]举报

caiyw 2023-04-19 10:19 00 [回复]举报

稳压泵启动的实际流量和启动时管道的压力有关系,正常情况启动补压时受管道压力影响,补压的流量是不会超过流量开关的动作流量因此是不会启动消防泵的。

冬临 2024-01-08 00:37 00 [回复]举报

流量开关是设置在高位消防水箱出水管上的,稳压泵的出水管可以在流量开关之后并入,这样稳压泵补水的流量就不会触发流量开关动作了。流量大的原因有一方面是补水的时候减少高位消防水箱的出水,避免流量开关误动作。

关闭

关闭

手机APP下载