娱乐场所在一,二,三楼时,厅室是否需要2小时的防火墙和乙级防火门与其他部位做分割?

娱乐场所在一,二,三楼时,厅室是否需要2小时的防火墙和乙级防火门与其他部位做分割?具体的规范要求在哪里?

舍之而后得 | 2023-03-21 22:12
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

消防黄河 2023-03-22 08:43 20 [回复]举报

建规,5.4.9.6 厅、室之间及与建筑的其他部位之间,应采用耐火极限不低于2.00h的防火隔墙和1.00h的不燃性楼板分隔,设置在厅、室墙上的门和该场所与建筑内其他部位相通的门均应采用乙级防火门。

aalwbw 2023-03-22 08:53 00 [回复]举报

建规5.4.9,第六条:厅、室之间及与建筑的其他部位之间,应采用耐火极限不低于2.00h的防火隔墙和1.00h的不燃性楼板分隔,设置在厅、室墙上的门和该场所与建筑内其他部位相通的门均应采用乙级防火门。

明亮晶莹 2023-03-22 09:52 00 [回复]举报

不是防火墙,而是防火隔墙。

建筑防火通用规范 GB55037-2022

4.3.7 歌舞娱乐放映游艺场所的布置和分隔应符合下列规定:
    1 应布置在地下一层及以上且埋深不大于10m的楼层;
    2 当布置在地下一层或地上四层及以上楼层时,每个房间的建筑面积不应大于200㎡;

    3 房间之间应采用耐火极限不低于2.00h的防火隔墙分隔;

    4 与建筑的其他部位之间应采用防火门、耐火极限不低于2.00h的防火隔墙和耐火极限不低于1.00h的不燃性楼板分隔。



yizhongdayang 2023-03-22 10:11 00 [回复]举报

《建筑防火通用规范》(GB55037-2022)4.3.7/歌舞娱乐放映游艺场所的布置和分隔应符合下列规定:

1 应布置在地下一层及以上且埋深不大于10m的楼层;    

2 当布置在地下一层或地上四层及以上楼层时,每个房间的建筑面积不应大于200㎡;    

3 房间之间应采用耐火极限不低于2.00h的防火隔墙分隔;   

4 与建筑的其他部位之间应采用防火门、耐火极限不低于2.00h的防火隔墙和耐火极限不低于1.00h的不燃性楼板分隔

另外,《公共娱乐场所消防安全管理规定(公安部令第39号)》第七条:

公共娱乐场所不得设置在文物古建筑和博物馆、图书馆建筑内,不得毗连重要仓库或者危险物品仓库;不得在居民住宅楼内改建公共娱乐场所。    

公共娱乐场所与其他建筑相毗连或者附设在其他建筑物内时,应当按照独立的防火分区设置;商住楼内的公共娱乐场所与居民住宅的安全出口应当分开设置。