加压送风系统风阀和风口问题?

请问大神楼梯间电梯间合用前室加压送风是用常闭风口吗?

如果采用常闭送风口是不是需要70℃电动常闭防火阀+百叶风口?或者常闭排烟阀+70℃防火阀+百叶风口?。

清浅 | 2022-11-07 15:17
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

周家斌 2022-11-07 16:43 10 [回复]举报

可以通过刘老师的讲解学习:前室顶送常开的加压送风口前加何种风阀? 之一:BEC防火阀 https://b.1190119.com/article-2878.htm

aalwbw 2022-11-08 09:22 00 [回复]举报

楼梯间的送风口为常开,前室/合用前室送风口为常闭。

清浅   回复: aalwbw2022-11-08 17:17

现在是阀门选用的问题,我这边是常闭风口

0    0 [回复]举报

米米果果 2022-12-15 17:37 00 [回复]举报

前室一般采用常闭风口。排烟阀一般是用在排烟系统中,前室送风时防烟系统。常闭送风口我记得好像是没有70度熔断功能的吧。

潘天坤 2024-07-01 14:43 00 [回复]举报

一般服务于超过2层的前室,应该设置常闭送风口,实现送风口常闭的方法不止一种,常见为设置手动开启装置使送风口常闭

这个区域一般属于未按防火分区独立设置竖向风管与每层水平风管交接的水平管段处,所以按照规范要求应该设置公称动作温度为70℃的防火阀

市场上是否存在常闭排烟阀或者常闭电动防火阀产品,本人不了解,不过本人认为:防火阀产品应该有型式检报告,现场材料应与报告一致。至于几种产品如何组合,只要能实现功能即可

建筑防烟排烟系统技术标准 GB51251-2017第3.3.6条规定:
加压送风口的设置应符合下列规定: 2 前室应每层设一个常闭式加压送风口,并应设手动开启装置