消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

余压监测系统

当住宅只有楼梯间和合用前室,没有走道,余压探测器改如何安装?

消防网友18738 | 2021-11-13 23:12
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

刘丽波 2021-11-16 08:29 10 [回复]举报

关于这个问题,一直没有定论。有人选择水电井,风井和室外作为走道,我个人觉得户内的压力是可以相当于走道内压力的,因为设这个系统的目的,主要是防止加压部位剩余压力过大时,疏散门无法打开。对于前室,无过道时,户门两侧的压力是我们应该监测的。但是取压点选择室内,似乎与住宅规范中,公共使用的管道应设于公共空间,有冲突!不知这个问题大家怎么看?

另外,对于本图的楼梯间,是否可以选择合用前室作为取压点,压差如何控制比较好?

阳光哥哥 2021-11-19 15:57 00 [回复]举报

现场情况前室的余压阀一般安装时开向疏散走道,楼梯间的余压阀一般开向前室!仅供参考

关闭

关闭

手机APP下载