消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问消防泵组零流量和150%流量时压力测试怎么测试

请问消防泵组零流量和150%流量时压力测试怎么测试,消防泵组性能测试怎么测试

BINGNAN | 2024-12-11 14:31
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

小唐12321 2024-12-11 17:04 00 [回复]举报

零流量把出水阀门关了,150就不懂了

jinyanwu 2024-12-11 17:18 00 [回复]举报

个人意见,仅供参考:

简单的说,在出口处安装一个阀门,阀门和泵之间安装一个压力表,管道上安装一个流量计。打开水泵,关闭阀门,测一下出口处压力,就是零流量压力;打开阀门,当流量等于额定流量的1.5倍时,测量一下出口压力是否为额定压力的65%,低于65%的就不合格。

影视 2024-12-13 11:07 00 [回复]举报

没有设计文件消防检测最有利的的设计压力怎么写

关闭

关闭

手机APP下载