消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

测试室内栓动压需要启泵吗?

从动压的定义来看,测试动压跟有没有启泵没关系,但是如果不启泵的话又无法满足0.35MPa的要求。求解惑

易bilibili | 2020-12-20 11:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

刘丽波 2020-12-20 13:03 20 [回复]举报

建筑消防设施检测技术规程

胖驹 2022-08-11 20:44 00 [回复]举报

7.4.12 本条规定了消火栓栓口压力技术参数。
    1 室内消火栓一般配置直流水枪,水枪反作用力如果超过200N,一名消防队员难以掌握进行扑救。DN65消火栓口水压如大于0.50MPa,水枪反作用力将超过220N,故本款提出消火栓口动压不宜大于0.50MPa,如果栓口压力大于0.70MPa,水枪反作用力将大于350N,两名消防队员也难以掌握进行灭火。因此,消火栓栓口水压若大于0.70MPa必须采取减压措施,一般采用减压阀、减压稳压消火栓、减压孔板等。


就这个条例的编制想法来说,动压应该是能够达到最大水压的情况。

关闭

关闭

手机APP下载