消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

20平方米左右的机房是否可以设置灭火器?

请教一下大家,一个20平方左右的机房能不能不设置气体灭火系统(自动灭火)而只设置满足灭火级别要求的灭火器?比如设置手推车式二氧化碳灭火器

心的自由 | 2023-06-27 16:50
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 11

安洪全 2023-06-27 17:03 00 [回复]举报

好像没有通过设置某种灭火器,可以实现替代“自灭”的。


灭火器用于初期火灾,且需要有人操作,并不能代替“自灭”


如果某机房仅设了灭火器,也是因为本身规模不大,火灾危险性不高,不需要设置“自灭”,而不是因为设置灭火器代替了“自灭系统”


像您描述的场所,可以考虑设置预制式的气体灭火系统,投入小,安装方便。

心的自由   回复: 安洪全2023-06-28 11:09

都是一些改造的项目,设置了气灭还得设置事故排风系统,甲方觉得投入太大,不想设。就想着能不能有其他的方法。

0    0 [回复]举报

宋奇   回复: 心的自由2023-06-29 10:32

可以考虑悬挂式温控释放的七氟丙烷,按照机房8%的浓度,一立方500g足够,算下来20kg的两个就够了。

1    0 [回复]举报

心的自由   回复: 宋奇2023-06-30 14:52

设置悬挂式七氟丙烷也要加事故排风吧?也要设泄压口?

0    0 [回复]举报

陈曲 2023-06-27 17:09 00 [回复]举报

看下规范是否属于全建筑必须设置自动灭火的情况 另外机房是否是特别重要场所 都不是就可以自由发挥了

心的自由   回复: 陈曲2023-06-28 11:11

这是改造项目,全建筑都设了自动灭火(喷淋系统),只是这次改造设置了一间机房。

0    0 [回复]举报

陈曲   回复: 心的自由2023-06-29 13:34

根据目前规范一般建筑只在特别重要设备间宜设置气体灭火 所以如果现在已经有自喷的话 综合经济因素 其实是可以不设置气体灭火系统的 

0    0 [回复]举报

同同不同 2023-06-27 22:08 00 [回复]举报

也可采用温控释放的悬挂式超细干粉灭火装置

心的自由   回复: 同同不同2023-06-28 11:12

机房用超细干粉的话,一旦喷放,那设备也就不能再用了吧!

0    0 [回复]举报

同同不同   回复: 心的自由2023-06-28 12:52

达到温控释放装置启动的温度的话,说明基本下边就着火了,20平米的小空间即便没有干粉,烟尘浓度也不小,再一个灭火救援为主,要真是特别重要的设备,可采用气体灭火系统

0    0 [回复]举报

牛疼 2023-06-28 14:25 00 [回复]举报

不能用消防器材代替消防设施。

当然甲方不想做就别做了呗,出了问题自己承担呗。

关闭

关闭

手机APP下载