火灾自动报警系统

隔离模块,手报按钮,广播算控制类设备,还是探测类设备,老师
冷风 | 2022-05-21 16:19
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

刘丽波 2022-05-21 23:20 00 [回复]举报

我不懂电气,斗胆判断不是探测类,请甄别。

周家斌 2022-05-22 09:05 10 [回复]举报

消防小学生刘振 2022-06-07 16:54 00 [回复]举报

隔离模块规范要求“系统总线上应设置总线短路隔离器,每只总线短路隔离器保护的火灾探测器、手动火灾报警按钮和模块等消防设备的总数不应超过 32 点;总线穿越防火分区时,应在穿越处设置总线短路隔离器”,当总线隔离器后端的线路出现短路,接地等情况时最多影响32个设备,出现故障状态,提高了火灾报警系统的可靠性,所以总线隔离器起到保护作用,既不属于控制类也不属于探测类。

手动火灾报警按钮:属于报警设备,需要通过手动启动,所以不属于探测类,同时手报按钮不能实现直接控制其他设备动作,所以不属于控制类

广播:广播音箱属于消防应急广播系统不属于控制类也不属于探测类,消防应急广播控制装置属于控制类。